Inverter generator

Discussion in 'Functional Gear & Equipment' started by thatclyde, Jan 18, 2020.


Tags:
  1. thatclyde

    thatclyde Monkey

    Using a Xantrex (Schneider Electric) XW4024 inverter. Currently using a 3500KW generator to maintain 1125AH batery bank along with 960 Watt solar. Can a 3500 Watt inverter generator be used with the current inverter? If the load is small and the 1/2 horse well pump comes on, will the generator increase its output fast enough to not cause a glitch?
     
  2. BTPost

    BTPost Stumpy Old Fart,Deadman Walking, Snow Monkey Moderator

    If that is the new nubers for the Trace SW4024’ then the Inverter will supplement the Genset when the load causes the genset to to drop below the Loe Frequency SetPoint... That is how my two Trace Inverters work...
     
  3. Cruisin Sloth

    Cruisin Sloth Special & Slow

    YES , just limit the gen support and charging amounts. 100 is full gen power , 35 is 35% of your stated KW that you program in
    Sloth
     
    Gator 45/70 and techsar like this.
  4. techsar

    techsar Monkey+++

    Yes...the battery bank will act as a buffer.
     
    Gator 45/70 likes this.
  5. Altoidfishfins

    Altoidfishfins Monkey+++ Site Supporter+

    Probably mis-typed it but a 3500 kW generator is one mighty big genset, would run a small to medium sized city. You must've meant 3500 W or 3.5 kW.
     
  6. thatclyde

    thatclyde Monkey

    Yep, 3.5kw.
     
    offgrittyt and Altoidfishfins like this.
  7. Navyair

    Navyair Monkey++

    Now THAT is some serious prepping! Keep smilin'
     
    Altoidfishfins and Gator 45/70 like this.